Wiring electrical outlets - 12 gauge wire, 20 amp breaker, 15 amp receptacles / outlets

Nifty

Super Self-Sufficient
Administrator
Joined
Nov 13, 2007
Messages
1,616
Reaction score
253
Points
237
I'm wiring my office and I have 12 gauge wire running throughout that goes to a 20 amp breaker.

I'd like to just use 15 amp receptacles / outlets, but it looks like they are designed for 14 gauge wire.

From what I've read, since I'm going to be using multiple 15 amp receptacles, it will be fine in this configuration.

One thing that stinks is that I have to pigtail the wire vs. just sticking it into the outlets back plugs. Pig-tailing / wrapping / curling 12 gauge wire sure is a pain!

Any thoughts or ideas?
 

HayZee518

New Member
Joined
Sep 11, 2013
Messages
66
Reaction score
1
Points
0
Location
Saint Regis Falls NY
get rid of the back wired outlets. you are just looking for trouble. sure its a pain to loop the wire ends for around the screws but you are better off in the long run. those beryllium springs loosen up and those wires can pull out!
 

Montyj

New Member
Joined
Sep 11, 2013
Messages
13
Reaction score
1
Points
0
I agree with Hayzee. NEVER use the stab in's. And if you use 15A outlets on a 20A circuit make sure you never exceed 15A over the entire circuit. The 15A rating applies to the entire outlet, including the strip between the screw terminals. An overload will cause that outlet to catch fire. Also do yourself a favor and do not pigtail the outlets. Power in on one set of screws, power out on the other. Pigtails with wire nuts are just one more connection to fail over time. It's electricity. Do it right the first time. Personally, I would always use 20A outlets on a 20A circuit because you never know what the future might require.
 

Smart Red

Lovin' The Homestead
Joined
Jan 10, 2012
Messages
329
Reaction score
47
Points
93
Location
Wisconsin
Around here, #15 wire is used only for lighting and #20 wire is required for outlets. IMHO it is well worth doing right. I always wrap the wire around the terminal. It takes a bit longer, but the connection will last.
 

HayZee518

New Member
Joined
Sep 11, 2013
Messages
66
Reaction score
1
Points
0
Location
Saint Regis Falls NY
I used to wire houses with a combination of #14 and #12. I found it cheaper in the long run to stock just #12 romex, then if I needed something larger, just to go get it.
 